I've run into a situation that I haven't encountered in my 20+ years of tech service. I've called the factory techs and they all agree that this problem can't be,,,,but it does.
This fryer has two heating elements. Each heater has 3 zones paralled with the other element. The first initial problem was that one of three zones was shorted causing an overheat problem. During troubleshooting I found a solid state relay to be closed. I replaced the solid state relay with an OEM part.
For a double check to make sure everything is okay, I take my voltage measurement across the line and load of each solid state relay. During the call for heat, I should get "0" volts. On two of the relays I get the "O" volts, but on the one I replaced I'm getting 120 volts. This is the part that other techs and I can't figure out. If the SSR (solid state relay) is in open condition, I get 208, but when it is closed, I get 120v which should be "O". All wiring looks and check out with the ohm meter, no opens or shorts within the heating elements.
I'm suspecting that the SSR is not good. Never ever encountered one that would only work half way. I ordered a new one from the factory, but delivery time is slow from this particular manufacture.
My question to the other techs, Have you ever encounterd a SSR to do this? Swapping it out with the others, the problem moves to the new space. So it has to be the SSR. Seems like there is always an odd wrench that gets throwed at me once in awhile that I've never seen coming.
The SSR is a single pole single throw, so it is not that difficult. Did a continuity check of the SSR during the call for heat and it goes to 0. Guess I'll have to wait and see until the new SSR comes in................SS
This fryer has two heating elements. Each heater has 3 zones paralled with the other element. The first initial problem was that one of three zones was shorted causing an overheat problem. During troubleshooting I found a solid state relay to be closed. I replaced the solid state relay with an OEM part.
For a double check to make sure everything is okay, I take my voltage measurement across the line and load of each solid state relay. During the call for heat, I should get "0" volts. On two of the relays I get the "O" volts, but on the one I replaced I'm getting 120 volts. This is the part that other techs and I can't figure out. If the SSR (solid state relay) is in open condition, I get 208, but when it is closed, I get 120v which should be "O". All wiring looks and check out with the ohm meter, no opens or shorts within the heating elements.
I'm suspecting that the SSR is not good. Never ever encountered one that would only work half way. I ordered a new one from the factory, but delivery time is slow from this particular manufacture.
My question to the other techs, Have you ever encounterd a SSR to do this? Swapping it out with the others, the problem moves to the new space. So it has to be the SSR. Seems like there is always an odd wrench that gets throwed at me once in awhile that I've never seen coming.
The SSR is a single pole single throw, so it is not that difficult. Did a continuity check of the SSR during the call for heat and it goes to 0. Guess I'll have to wait and see until the new SSR comes in................SS