I have a panel that supports 2 30 amp cords. At marina only have access to one 30 amp twist lock outlet and one 20 amp outlet have 2 cords plugged in one with pigtail adapter (about 1 foot long) when I set panel to 1 line and turn on battery charger no problem when I set panel to 2 lines it trips breaker on boat panel tried reversing cords at dock swapped pigtail and still did the same thing. Any advice welcome
 

Bondo

Moderator
Staff member
Joined
Apr 17, 2002
Messages
71,307
At marina only have access to one 30 amp twist lock outlet and one 20 amp outlet have 2 cords plugged in one with pigtail adapter (about 1 foot long) when I set panel to 1 line and turn on battery charger no problem when I set panel to 2 lines it trips breaker on boat panel

Ayuh,.... Welcome Aboard,.... Just a guess, but I'm thinkin' both yer power cords are run from the same leg of the shore panel, when ya combine 'em, it's a dead short,....
 

alldodge

Moderator
Staff member
Joined
Mar 8, 2009
Messages
43,318
It could be your panel is picking up a ground fault. Are you using 3 prong plug on 20 amp outlet?
 

Grandad

Lieutenant Commander
Joined
Jun 7, 2011
Messages
1,504
If your system has a common neutral connection between the two power supplies, a very small imbalance in neutral current to line current (.005 amp) could cause a GFCI to just do its job and trip as designed. - Grandad
 