Re: Alpha One Gen II Question---- Electrical problem
Further more, I'll assume you are somewhat comfortable with electricity considering you said you pulled the panel in the boat.
If the problem is present in the house panel WITH THE BOAT DISCONNECTED you'll need to isolate if its your circuit or the one coming into the house from the power company.
To check that, kill the mains in the house panel. Switch your meter to ohms and start checking
Neutral to ground should be very low resistance
Hot to neutral should read open or close to it, as should hot to ground.
Test hot on the de-energized side of the main breakers only. If your not following what I'm getting at here call a electrician. You can blow up your meter and get hurt if you run power through the ohms setting on your meter.
Further more, I'll assume you are somewhat comfortable with electricity considering you said you pulled the panel in the boat.
If the problem is present in the house panel WITH THE BOAT DISCONNECTED you'll need to isolate if its your circuit or the one coming into the house from the power company.
To check that, kill the mains in the house panel. Switch your meter to ohms and start checking
Neutral to ground should be very low resistance
Hot to neutral should read open or close to it, as should hot to ground.
Test hot on the de-energized side of the main breakers only. If your not following what I'm getting at here call a electrician. You can blow up your meter and get hurt if you run power through the ohms setting on your meter.