hrdwrkingacguy
- Mar 9, 2010
- 368
Re: Carrier A/C, Again!
The valve will try to maintain whatever superheat you set it to...I wouldn't think you even need to adjust it...What you are trying to accomplish is around 12 degrees superheat(68-70# suction pressure with a 50 - 52 degee suction line temperature) and then have 8 to 10 degrees subcooling...If the valve is set to 12 degrees(which should be what it starts at) and you have 4 degrees of subcooling you are undercharged...If you have 12 degrees of superheat and 25 degrees of subcooling you are overcharged...
The main question in any refrigerant diagnosis is "Where is the liquid"
Since you superheat vapor and subcool liquid, high superheat means high vapor...And vapor doesn't move heat, liquid does...Less superheat means you are flooding back liquid to the compressor...So target superheat is 10-12 degrees at the indoor coil...
Since you subcool liquid target subcooling is around 9 degrees...High subcooling means high liquid level in the condenser, and since liquid in the condenser already gave up its heat, excessive liquid is useless and limits space in the coil for it to do work...
Essentially you are looking for just enough subcooling to keep a solid column of liquid in the liquid line, and enough superheat to ensure that the compressor is seeing only vapor in the suction line...
Gawd where is a dry erase board when I need one...
PS by way of setting superheat and subcooling you are controling where the state change occurs at...to much superheat and the state change happens to early and since vapor doesn't move heat you lose capacity...To much subcooling and the state change occurs to early and you stack up liquid in the condenser and lose capacity...