Master Chief Petty Officer
- Joined
- Oct 13, 2009
- Messages
- 860
Hey everyone ,
I have a Yard question for you guys and frankly I don't have the energy to start on another forum and I know folks on here are sharp.
This is regarding my sprinkler system . My back yard lawn is struggling this year and my sprinklers don't have the coverage they once did.
So I hook up a pressure gauge to my front yard , backyard , and water heater bibs And on all of them I have 85 ish psi
If I turn on a sink or shower it drops maybe 10
Turn on my front yard sprinklers , it drops maybe 5 ,But front yard sprays great . From what I can tell , the front sprinklers don't run through the house , it's split from the main so not affected by house
Now the back yard . I turn on my smallest zone and it drops to 35 ! Ouch . No wonder I am getting no coverage .
Right now I have those old style gates type valves . One for the main house shutoff , and the other for my back yard sprinklers .
My thought is that is too much drop from 80 psi and these valves are restricting flow ....... Do you think I would not get so much drop if I swapped in ball valves ?
They worked better a few years ago , maybe my valves are clogged or something ?? Thoughts
I have messed with regulator and can't get higher than 80-85
Please excuse brevity I am on my cell
Thanks
I have a Yard question for you guys and frankly I don't have the energy to start on another forum and I know folks on here are sharp.
This is regarding my sprinkler system . My back yard lawn is struggling this year and my sprinklers don't have the coverage they once did.
So I hook up a pressure gauge to my front yard , backyard , and water heater bibs And on all of them I have 85 ish psi
If I turn on a sink or shower it drops maybe 10
Turn on my front yard sprinklers , it drops maybe 5 ,But front yard sprays great . From what I can tell , the front sprinklers don't run through the house , it's split from the main so not affected by house
Now the back yard . I turn on my smallest zone and it drops to 35 ! Ouch . No wonder I am getting no coverage .
Right now I have those old style gates type valves . One for the main house shutoff , and the other for my back yard sprinklers .
My thought is that is too much drop from 80 psi and these valves are restricting flow ....... Do you think I would not get so much drop if I swapped in ball valves ?
They worked better a few years ago , maybe my valves are clogged or something ?? Thoughts
I have messed with regulator and can't get higher than 80-85
Please excuse brevity I am on my cell
Thanks