Sorry for the long delay. Out for work and could not get back to the furnace until now.
Dolluper - The thermostat had been acting funny for a number of years in that it was hard to set the temp. Had to work the up and down buttons to try to get it to move. Lived with it since I did not make changes often, but with this work I just got tired of it so I replaced it.
I am losing patience with this problem, but I think I am closer now.
When I call for heat it looks like everything works right. Inducer fan now starts, pilot lights, and the time delay relay waits for about 40 seconds before it applies 24vac to the main gas valve.
If the valve is connected this is when the 24v transformer fuse blows. If I disconnect the valve (lead 1 on the valve) there is 24v on the lead and the fuse does not blow.
I believe the lightening strike damaged the solenoid and this is blowing the fuses.
Thoughts anyone? How often does this happen? How hard & expensive is it to replace it?
Furnace & valve have the following numbers:
Furnace: model 58SSL095-CC
Valve: Model 36E93 and has a number on it EF32CB197A
Book for the furnace says the valve is a White Rogers 36E.
I think it is this one, but not sure:
http://www.patriot-supply.com/products/showitem.cfm/WHITE_RODGERS_36E93_304
Thanks in advance for everyone who has been helping with this.